Hot Gas Bypass Valve Application and Low Load Conditions

Поделиться
HTML-код
  • Опубликовано: 5 сен 2024
  • Hot gas bypass valve operation is utilized in low load applications and conditions. Hot gas bypass puts a false load on the evaporator when the indoor temperature drops off, this helps to prevent short cycling of the compressor in low load applications.
    Save 8% on your purchase www.trutechtoo... with promo code knowitall
    Check out the HVAC Know It All app app.hvacknowitall.com
    Visit HVAC Know It All on social media Facebook
    / hvacknowitall
    Instagram
    / hvacknowitall1
    LinkedIn / gary-mccr. .
    Listen to the HVAC Know It All Podcast anchor.fm/hvac...
    Visit www.hvacknowit... for articles, and tips
    #hotgasbypassvalve #refrigeration #hvac

Комментарии • 112

  • @HVACKnowItAll
    @HVACKnowItAll  3 года назад +5

    I love hot gas bypass valves 😆

    • @abazism
      @abazism 4 месяца назад

      Can you please make a video on head pressure control valve please.

  • @drew2276
    @drew2276 3 года назад +1

    i get my gf to run flat after I raise her temp by backing out the screw through an open device, I screw in and out to back tension off, I have some superheat added into that, it gets warmer less chance that will cycle off, and back to normal conditions naturally on its own. I back off again and discharge my load in the theater. the load drops off because the body heat is gone. but I set for that. so that in a nutshell is how I adjust her full capacity attitude and generally a good example of an application of that. happy HVAC guys!

  • @robertmalone9699
    @robertmalone9699 3 года назад +3

    Your explanation was thorough yet simple and to the point. You didn't try to crowd too much information into video.

  • @NotThatGuy_YepThatGuy
    @NotThatGuy_YepThatGuy 2 года назад +1

    I struggle with mechanical load and ambient control. Specifically the applications of Hot Gas bypass and Headmaster Valves. I mostly understand what they do, and why, but i have the damndest time troubleshooting if they are the problem.
    Thanks for this video. Long time watcher, seldom commentor.

  • @renecuevas4128
    @renecuevas4128 Год назад

    I see and read most of the comments Most guys understand quick. Others have No clu n got it confused w Txv. U explain it clear. I m not American n clearly understand ....fl weather around 60 s Good time for LAT and Low Load u put an easy Movie Theater example. Tnks n blessings

  • @VapourRose
    @VapourRose 3 года назад +3

    We use the same pipe set up but use a rapid cycle solenoid and no HGBV to control really tight temperatures in our environmental rooms.

    • @HVACKnowItAll
      @HVACKnowItAll  3 года назад

      Cool!

    • @Thiscutepup
      @Thiscutepup 2 года назад

      Do you use a PLC to control the toggle cycle of the solenoids? Or is it controlled by a relay?

    • @VapourRose
      @VapourRose 2 года назад +1

      @@Thiscutepup we use a Loop controller and a relay to cycle it on and off. Company be buy the controllers from is called Future Design control and its the R-22 controller.

    • @Thiscutepup
      @Thiscutepup 2 года назад

      Thanks! I took a look at the website and the controllers they offer. Never heard of this company, but they type of controllers look like a nice drop in for Watlow controllers. I really like the Watlow controllers, but they are very expensive. Most customers don’t need the amount of features either. What I have found out is toggling solenoids works well, however some size units need an adjustable valve inline with the solenoid to meter the amount of hot gas entering the evaporator. This way to can adjust the Hot Gas Bypass Valve to the exact PSI that you want. I watch the controller to see the temp swing. I want to mention that Hot Gas is not greatly energy efficient, although the machines run really well when not cycling and can maintain a consistent temp inside the evaporator. We can hold a temp of -+.5 degrees on oil and water cooling. This helps our customers achieve ultra precision in their processes.

  • @chrisnorris1959
    @chrisnorris1959 3 года назад +1

    Thanks Gary! Great explanation. Watching this video will make the actual Sporlan literature for these valves easier for me to digest.

  • @mikefreedom5612
    @mikefreedom5612 3 года назад +1

    Good video! It's a way to balance the load on small refrigeration systems

  • @mikhaielj846
    @mikhaielj846 Год назад

    Thanks so much needed this for tomorrow’s job

  • @epicone2449
    @epicone2449 3 года назад +2

    Great videos man. Listen to your podcast too. Thank you for what you do for the trade

  • @sdsd4284
    @sdsd4284 3 года назад +2

    So technically its job is similar to a epr and a headmaster ? Great vid and EXPLANATION btw u make it very understanding.

    • @HVACKnowItAll
      @HVACKnowItAll  3 года назад +1

      Not really a head master maintains head for low ambient and an EPR is on the outlet of the evaporator

  • @abazism
    @abazism 4 месяца назад

    Wow very well explained.

  • @michaelbalke2314
    @michaelbalke2314 3 года назад +1

    Great explanation of the system!

  • @bhunter3850
    @bhunter3850 3 года назад +1

    Thanks for the knowledge. I think I’ve learned more from your videos than my coworker who considers himself a “super tech”.

  • @daviddesilva4971
    @daviddesilva4971 3 года назад +1

    Great explanation on the hot bypass valve. Thxs for the vids!

  • @shockiller465
    @shockiller465 3 года назад +1

    Thank you sir; Great Video keep up the good work

  • @johnpolos8796
    @johnpolos8796 2 года назад +1

    Have you worked on environmental test chambers and chillers?

  • @shanegreen268
    @shanegreen268 3 года назад +1

    Thank you for sharing your knowledge. Great video

  • @Jeff-Lawrence
    @Jeff-Lawrence 3 года назад +1

    Love this style of vid. Great work

  • @mdmuntasiralam774
    @mdmuntasiralam774 10 месяцев назад

    Great demonstration! Thank you very much. What's the purpose of the pressure equalization line here?

  • @andrewnolan8449
    @andrewnolan8449 Год назад +1

    One of the very important part on hot gas defrost missing …

    • @HVACKnowItAll
      @HVACKnowItAll  Год назад

      This is not hot gas defrost, it's hot gas bypass

  • @joeschneider67
    @joeschneider67 2 года назад +1

    Thanks

  • @sintongbutarbutar8478
    @sintongbutarbutar8478 3 года назад +1

    Very clear explanation, thx

  • @nimbo9492
    @nimbo9492 2 года назад +1

    I have seen some hot gas bypass lines connected to the suction line (in between compressor and evaporator) as opposed to inlet evaporator like in this video. How are they exactly different?

    • @renecuevas4128
      @renecuevas4128 Год назад

      Same question i got when i see his Diagram seems like same Line ......but doing different case scenario as he mentioned Movie Theater....Low Load versus LAT make sense i guess ....

  • @stefanocubero6367
    @stefanocubero6367 2 месяца назад

    Thanks man!

  • @maheradous9257
    @maheradous9257 8 месяцев назад

    Good job

  • @fret2fret221
    @fret2fret221 3 года назад +1

    The way you explained this sounds like it operates similar to a TXV...

    • @HVACKnowItAll
      @HVACKnowItAll  3 года назад

      Not exactly, TXV opens on a rise in bulb temperature. A hgb valve opens on drop in suction pressure.

  • @Billo1281
    @Billo1281 2 года назад

    Very well explained. Thanks!

  • @simohvac9222
    @simohvac9222 3 года назад +1

    good explanation thanks

  • @janeilquino2599
    @janeilquino2599 3 года назад

    Good day sir.thanks for information very clear explanation

  • @natepeterson7145
    @natepeterson7145 3 года назад +1

    Well done!

  • @neilvestervictor180
    @neilvestervictor180 3 года назад +1

    great information knowledge is the key to success

    • @HVACKnowItAll
      @HVACKnowItAll  3 года назад +1

      Yes it is, thank you

    • @neilvestervictor180
      @neilvestervictor180 3 года назад +1

      I am a chill water technician from st Lucia

    • @HVACKnowItAll
      @HVACKnowItAll  3 года назад

      Lovely weather I bet!

    • @neilvestervictor180
      @neilvestervictor180 3 года назад +1

      yes sunny in the Caribbean with a little rain in between you should take the trip on a vacation lol

    • @HVACKnowItAll
      @HVACKnowItAll  3 года назад

      Yes but our conrona restrictions re-entering are crazy so no traveling for a while.

  • @mr.fahrenheit723
    @mr.fahrenheit723 2 года назад +1

    This is a great video!

  • @chova210
    @chova210 10 месяцев назад

    Well explained 👏

  • @chantaledamiengatien725
    @chantaledamiengatien725 3 года назад +2

    Hi,
    Great video !
    I have also a hot-gas bypass valve on my LG multisplit, but it is bypassing directly the compressor's output to the input of the accumulator (just before the compressor input).
    When the hot-gas is activated, for example when a split is stopped, I can see the high pressure decreasing and the low pressure increasing.
    However, what is strange to me, is that when the hot-gas is deactivated after 30 seconds, the high-pressure recovers quite fast its initial value, but the low pressure is dropping much lower than its initial value (for example, from 8.3 bars to 6.7 bars) and seems to stay at this lower value (until the outdoor unit regulation is changing the inverter compressor speed).
    Do you have some explanation why it behaves like that ? I am not really sure that it is normal since it is generating periodical fluctuations of the regulation :(
    Thanks a lot and regards

  • @ollirbasepeacefulmusic6508
    @ollirbasepeacefulmusic6508 Год назад

    Why you don't see hot gas bypass to use as defrost in domestic fridge or freezer? My dad use to have an old fridge with hot gas bypass defrost

  • @henryperez5404
    @henryperez5404 2 года назад

    Hey question to close it I have to counter clockwise rite?

  • @723lion
    @723lion 3 года назад

    HGBV is for tight temperature control.

  • @mahmudnady1859
    @mahmudnady1859 3 года назад

    Thanks for the information

  • @juvaeljadman2296
    @juvaeljadman2296 Год назад

    Good day sir. What is the actual low pressure of -10 and what is the deffirential walk in chiller. Thank for your help

  • @syedbasheer8210
    @syedbasheer8210 3 года назад +1

    Good explanation👉

  • @sholapuramtoday1596
    @sholapuramtoday1596 Год назад

    If discharge high pressure and high temperature that time not use this please explain

  • @Boz1211111
    @Boz1211111 Год назад +1

    seems like it wastes energy not to cycle compressor?

  • @dinushakumara4580
    @dinushakumara4580 2 года назад

    is this condition liquide refrigerant may be come back to the compressor

  • @oriansinkleryukon2680
    @oriansinkleryukon2680 Год назад +1

    What actually shuts cooling down will the hot gas bypass continue to run when show is over

    • @HVACKnowItAll
      @HVACKnowItAll  Год назад +1

      If it hits full on set point, the system will shut down. The hot gas will stop feeding on the off cycle.

  • @user-sy5we4jo3o
    @user-sy5we4jo3o 2 года назад

    Can i replace the sporlan hot gas bypass valve with a solenoid controled by a digital tempreature sensor
    The sensor will measure suction line temp and control hot gas bypass valve

  • @herbertfynnwilliams5177
    @herbertfynnwilliams5177 2 года назад +1

    I have questions? am working on a unit that has hot gas valve when you put the unit on the temperature is able to come down to about 19/c but when the hot gas comes on you have the temperature reading 23 and it doesn't come down any more

    • @HVACKnowItAll
      @HVACKnowItAll  2 года назад

      These are room temps? Hot gas is for low load conditions. It needs to be set to supply hot gas when the load and corresponding evap pressure falls off.

  • @mematyi
    @mematyi 2 года назад

    Great Explanation!
    Could you make a video explaining the difference between this Hot-gas bypass valve method and the Evaporator pressure regulator (Danfoss KVP)? Is it technically the same?

  • @aircooledchilleralltypes4938
    @aircooledchilleralltypes4938 3 года назад

    But what is the function of the equlizer line

  • @arazqurbanov8162
    @arazqurbanov8162 6 месяцев назад

    Salam size bir sualim var?
    Valve soyuq hava seraitnde isleye biler

  • @sumantaparamanik7863
    @sumantaparamanik7863 2 года назад

    It can be use Blast Freezer? Plz explain me

  • @mrgreen9086
    @mrgreen9086 3 года назад +1

    Great explanation is this system factory or do some components needs to be field installed?

  • @ramilolanda8517
    @ramilolanda8517 2 года назад

    How do bypass valve of expansion valve works?

  • @fret2fret221
    @fret2fret221 3 года назад

    The guy training me saw one of these the other day and legit said “I’ve never seen anything like that before...” 🤦‍♂️

    • @tonydellapennajr2681
      @tonydellapennajr2681 3 года назад +2

      You're dragging the guy training you because he hasnt seen something?

  • @Sigmameals
    @Sigmameals 3 года назад

    Will you be able to put what you explained on a PH diagram or in equation forms using thermodynamic cycle?

  • @bradmironik6137
    @bradmironik6137 3 года назад +1

    Good video. I follow on how the hot gas creates a load on the evaporator but is there another component after such as an accumulator to return the refrigerant back as a vapor? I haven't seen this setup in the field before. Thanks.

    • @HVACKnowItAll
      @HVACKnowItAll  3 года назад

      There is never a receiver after an evaporator, the receiver is after the condenser. It's still returning as a vapour, the discharge gad is highly superheated vapour

    • @HVACKnowItAll
      @HVACKnowItAll  3 года назад

      Sorry my bad, thought you said receiver but none the less no vapour will get back during hot gas byapss

    • @bradmironik6137
      @bradmironik6137 3 года назад

      Thanks for responding. So you are saying the hot gas in the evaporator has some heat removal but not to the point of changing state? Therefore vapor still returns to the low side of compression.

    • @capitolrefrigerationheatin7501
      @capitolrefrigerationheatin7501 3 года назад

      @@HVACKnowItAll I see accumulators after evap to catch any liquid,saves compressor from slugging

    • @Username-ng8jy
      @Username-ng8jy 3 года назад

      Yes those are common in refrigeration. I used to do commercial refrigeration. It was a vital component especially freezers where the coil must be flooded with liquid for below zero temps.

  • @harendradangwal6382
    @harendradangwal6382 2 года назад

    Hot gas bypass valve in Air dryer not allowing to transfer the Cold refrigerant into evaporator why? transfer hot refrigerant into evaporator

  • @jasonjohnsonHVAC
    @jasonjohnsonHVAC Год назад

    RAWAL DEVICE WOULD BE GOOD IN THIS EXAMPLE

  • @peterrivas08
    @peterrivas08 3 года назад

    Really good video but could you or someone please explain the difference between this and a headmaster valve? Are they essentially they same just different terms? Thanks

    • @ES-ml4cg
      @ES-ml4cg 2 года назад +1

      Headmaster or OROA is for head pressure control at low ambient conditions.

    • @peterrivas08
      @peterrivas08 2 года назад

      @@ES-ml4cg thank you for the reply. Sorry I'm just confused, but why do you need to keep the head pressure up? So the low side stays up as well?

  • @Sorcerers_stash
    @Sorcerers_stash 3 года назад +1

    Good stuff

  • @pangmlrani5200
    @pangmlrani5200 3 года назад +1

    Does the compressor delivery pressure becomes less when bypass valve is open?

    • @HVACKnowItAll
      @HVACKnowItAll  3 года назад

      No it becomes more, it's adding pressure the to suction line

    • @HVACKnowItAll
      @HVACKnowItAll  3 года назад

      But on the discharge line the pressure will drop a little, sorry, not exactly sure what you're asking.

  • @mkamal2892
    @mkamal2892 2 года назад +1

    how does hot gas bypass work??

  • @Coonhoound89
    @Coonhoound89 3 года назад

    Awesome

  • @arazqurbanov8162
    @arazqurbanov8162 6 месяцев назад

    Salam

  • @fret2fret221
    @fret2fret221 3 года назад

    The way you explained this sounds like it operates similar to a TXV...

    • @Username-ng8jy
      @Username-ng8jy 3 года назад +1

      Nah dude. Nothing at all lol. A txv is there to throttle liquid into evap to provide cooling.
      This is just a valve that allows heat to enter the low side to increase pressure a bit when there is no load.