HVAC tech here, looks good to me for a diy job. Only thing I would say is to have the gas pressure tested with a manometer to insure the correct pressure is entering and exiting the valve. Pipe wrenches come in handy when working on gas valves and lines.
Just had this exact problem. $188 for the Honeywell gas valve which had to be shipped to our guy. And labor was $162. That was including the 3 days where he came out to diagnose. $375 total.
If I were you, I would either call back the service company or invest in a manometer to check your 1st + 2nd stage manifold gas pressure to be safe. The factory will usually get pretty close, but sometimes it can be off by 30%.
You're wrapping the tape backwards. Wrap it the same direction you screw on the valve which is clockwise in this case. Otherwise it can unwind when you screw it in.
HVAC technicians are like mechanics they take advantage of your ignorance and markup everything. It’s disappointing. As soon as people learn how to do things themselves, you see them posting hate. Kudos my friend!
No we don't. Us techs don't make the pricing. We charge what our companies make us charge. You think we are out there to screw over the customers that keep us in a job? We actually think the cost of repairs we have to charge is ridiculous. At least us good techs anyway
@DadItYourselfDIY a good tech will do that. We would rather provide knowledge than anything. I've walked people through fixing thier furnaces over the phone on after hours just to try and save them the cost of after hours service call fees
you should check manifold pressure to be sure you don't risk carbon monoxide, and also soot buildup which could mean a future heat exchanger replacement if it cracks from uneven expansion
@@DadItYourselfDIY It should be written on the furnace unit in inches WC as manifold or outlet pressure, not to be confused with inlet pressure. If not then look in the manual. The reason why it needs to be adjusted is that natural gas is not always the same pressure or flow rate. Depending on the building and pipes used, you can have different amounts of restriction.
I got sorta the same model, Brant's came out and told me it's gonna cost me $400+ parts, I've never tried to install one myself, But being a single income family of 4. I can't afford that. The part alone is only $130, The guy told me it would be around $300 for just the part... But it wouldn't be in until next week and then wouldn't be able to install it until next friday. But like I said I looked it up, Saw the part for $130. What should I do?
I ordered mine from Amazon and had it the next day. I cannot tell you what to do. If you are mechanically inclined, then it's something you can handle. If you are unsure about any of the steps, then ypu should let a professional do it.
@@DadItYourselfDIY Hello I really like this video. Very well done and informative. I am going to replace the valve on my furnace. I was wondering since it seems to have been a while, when were you going to post the follow up video. I would be most interested in seeing it and learning more.
I was quoted $600 plus parts to replace. The service call was $150. I bought the valve for $100 on Amazon Prime. So me doing it was about $250. Had I had them order the part and install it, it would have been, $150+$100+$600. So, I save $600 (assuming they didn't mark up the parts)
@@DadItYourselfDIY $600 dollars for parts 😳!!! That's beyond ridiculous!! They were trying to charge you $600 dollars for a hundred dollar valve, some pipe dope and tape 🤦. Like seriously how do those people sleep at night when they're robbing people like that.
There's no way that I would pay someone $800 dollars to do this job. HVAC technicians are like car mechanics. They 100% overcharge for their work. My gas furnace ignitor knob recently broke because it's made out of cheap plastic. If I would have called a HVAC technician to fix it they most likely would have attempted to replace the entire valve instead of installing a new knob. I was reading online that they have to replace the entire valve because of regulations which im sure would have costed $500-$800. I purchased 2 replacement knobs for $10 dollars online. An aftermarket company makes replacements. I didn't see any replacement knobs from the manufacturer that makes the valve which im sure they do on purpose for profit and regulations. They want you to spend a bunch of money not replace a $10 dollar plastic knob. The aftermarket knob looks and works identical to the oem knob. The aftermarket knob manufacturer made a smart business decision to make those knobs because it probably only costs them a couple dollars to make them and it's something that people need. Personally if I was you I would have purchased and used some pipe dope. It's super cheap so there isn't a good reason not to use it. I also recommend spraying the lines better with water that has a good amount of dawn dishwashing liquid in it. I'm a pipefitter so I can honestly tell you that it's common for people to get leaks so you definitely want to use thread Seal Tape, pipe dope and spray it down really good with dawn dishwashing liquid/water. You honestly made a smart decision doing it yourself. Most issues with central air units and furnaces are things that you can fix on your own as long as you do some research with online videos. I've fixed multiple of these issues on my own. Back in the 90's you would have had to call a HVAC technician but now there's information and replacement parts online. I even replaced my furnace fan on my own. A HVAC technician would have probably expected me to buy an overpriced fan of their choosing and charged me hundreds to install it. If someone is considering doing this stuff on their own they need to make sure that the electric and gas are completely shut off. If you shut the electric and gas line off, find good deals online for replacement parts and watch videos it's totally worth doing it on your own. I found an used replacement fan online that looked nearly new and it saved me a ton of money. Charging $800 dollars to fix your gas valve is beyond ridiculous! $800 dollars for a hour long job is crazy! They probably purchase the parts for a cheaper price than normal, they would have drove 15min to get to your house, spent 30min to install it and another 15min to drive back to their shop so they definitely don't deserve $500-$800. I could understand if it was $300 because the valve might be $100 dollars and then $150-$200 dollars for a hour of their time but definitely not $800! What HVAC technician companies don't understand is that they lose money for charging so much because a lot of people decide to do it on their own to save money. If they would have charged you $300-$400 you probably would have decided to have them install it and they would have still made a good profit for their time.. I'm guessing a gas valve would be $50-$200 dollars so charging more than $400 dollars for the job is ridiculous. That's my personal opinion.
Another thing to consider is whether you’ll even be saving any money attempting this DIY yourself. Gas valve testing and replacement requires specialty tools, equipment and material that can really add up. And some of the tools and material you may not use again, unless of course you have to replace another valve. Learning how to use these tools and materials and testing and replacing the valve itself is also a time-consuming process. A furnace gas valve making noise will require different tools and techniques than a gas valve with an electrical issue. By the time it’s all said and done, a job that would most likely take you a day or two can be done safely and professionally by an HVAC professional in much less time.
A gas manometer is $50, a couple of pipe wrenches is $30, pipe dope and tape is probably $20 and the gas valve is probably around $80-$200 dollars. That's only around $200-$250 dollars which is much better than $800 dollars!!! There's plenty of videos online that teaches you how to do it. I would much rather spend a hour of time and spend $200 than to pay someone $800. I'm a pipefitter though so messing with threaded pipe and gas lines is something that I do for a living. A HVAC technician already owns those tools so charging $800 to replace this valve is ridiculous. I definitely would have replaced it on my own. I think that at least 1/3-1/2 of the population is smart enough to turn off the electric, gas and watch a couple of videos to install it themselves. Half of the population on the planet probably doesn't have enough common sense to shut off the gas/electricity or to properly tighten the pipes so I understand why some people are better off calling HVAC technicians. I understand that HVAC technicians are hard working people that are trying to make a living but $800 for this valve replacement is ridiculous. Just my opinion.
Pipe Dope I Highly recommend for Gas lines Connections. That yellow tape it doesn't hold Up 😊
Good to know. Rectorseal?
HVAC tech here, looks good to me for a diy job. Only thing I would say is to have the gas pressure tested with a manometer to insure the correct pressure is entering and exiting the valve. Pipe wrenches come in handy when working on gas valves and lines.
Same as I was thinking. Also. He's lucky it's natural gas and not LP gas, or else he could really cause some damage without a manometer.
The HVAC tech that did my troubleshooting verification didn't say anything about a manometer. What is that?
@@DadItYourselfDIY it’s used to check gas pressures
@@craigbraswell4269what kind of damage are you talking about
Yeah?
Good video on replacing the valve. After seeing how it is done. I can decide whether to tackle this or call HVAC for a quote.
Exactly!
Just had this exact problem. $188 for the Honeywell gas valve which had to be shipped to our guy. And labor was $162. That was including the 3 days where he came out to diagnose. $375 total.
Not a bad price.
If I were you, I would either call back the service company or invest in a manometer to check your 1st + 2nd stage manifold gas pressure to be safe. The factory will usually get pretty close, but sometimes it can be off by 30%.
Great advice.
just wondering if you should check the outlet gas pressure on the gas valve?
The pressures were preset on the valve and marked. Seemed pretty straightforward. But I'll research that.
Get a bench vise. Can have bolts with wing nuts, lock washers so you can install/remove vise when you need it. Just a idea 💡. 👊✌️
I need to get a permanent bench first!
You're wrapping the tape backwards. Wrap it the same direction you screw on the valve which is clockwise in this case. Otherwise it can unwind when you screw it in.
It's confusing, but I got it right in the end.
HVAC technicians are like mechanics they take advantage of your ignorance and markup everything. It’s disappointing. As soon as people learn how to do things themselves, you see them posting hate. Kudos my friend!
Thank you for that. While I'm not an HVAC tech, I do have training in very similar systems.
No we don't. Us techs don't make the pricing. We charge what our companies make us charge. You think we are out there to screw over the customers that keep us in a job? We actually think the cost of repairs we have to charge is ridiculous. At least us good techs anyway
@techdaddy7955 I agree, it was definitely his company. He literally told me how to fix it, saving a ton of money.
@DadItYourselfDIY a good tech will do that. We would rather provide knowledge than anything. I've walked people through fixing thier furnaces over the phone on after hours just to try and save them the cost of after hours service call fees
@techdaddy7955 That's super cool!
you should check manifold pressure to be sure you don't risk carbon monoxide, and also soot buildup which could mean a future heat exchanger replacement if it cracks from uneven expansion
Saw that in the comments. I have a manometer on the way. My furnace is out in the garage, so there is that.
@@DadItYourselfDIY it's probably within 10% of spec already, but its good to be safe
@elektrokinesis4150 Agreed!
@elektrokinesis4150 Is it standard or do I need to look in the manual for the inlet and outlet pressures?
@@DadItYourselfDIY It should be written on the furnace unit in inches WC as manifold or outlet pressure, not to be confused with inlet pressure. If not then look in the manual. The reason why it needs to be adjusted is that natural gas is not always the same pressure or flow rate. Depending on the building and pipes used, you can have different amounts of restriction.
Thanks for the video. I noticed that you didn’t adjust the gas valve pressure on the replacement.
I did not. I don't have a "manometer"
Good video
Thank you!
Can’t stop a GOODMAN!
No you can not!
I got sorta the same model, Brant's came out and told me it's gonna cost me $400+ parts, I've never tried to install one myself, But being a single income family of 4. I can't afford that. The part alone is only $130, The guy told me it would be around $300 for just the part... But it wouldn't be in until next week and then wouldn't be able to install it until next friday. But like I said I looked it up, Saw the part for $130. What should I do?
I ordered mine from Amazon and had it the next day. I cannot tell you what to do. If you are mechanically inclined, then it's something you can handle. If you are unsure about any of the steps, then ypu should let a professional do it.
That’s a new valve it really needs the gas pressure checked and set. Purchase a manometer.
Already ordered one. Follow-up video next week.
@@DadItYourselfDIY Hello I really like this video. Very well done and informative. I am going to replace the valve on my furnace. I was wondering since it seems to have been a while, when were you going to post the follow up video. I would be most interested in seeing it and learning more.
Lots of Ryobi stuff I noticed.
I have a couple of their tools.
How much money did you save
I was quoted $600 plus parts to replace. The service call was $150. I bought the valve for $100 on Amazon Prime. So me doing it was about $250. Had I had them order the part and install it, it would have been, $150+$100+$600. So, I save $600 (assuming they didn't mark up the parts)
@@DadItYourselfDIY $600 dollars for parts 😳!!! That's beyond ridiculous!! They were trying to charge you $600 dollars for a hundred dollar valve, some pipe dope and tape 🤦. Like seriously how do those people sleep at night when they're robbing people like that.
Hello handsome much time without see your videos
🤦♂️
All that is exactly what should not be done
Thanks for watching! It's been a year and I haven't died or blown my house up. So I guess I got lucky!
There's no way that I would pay someone $800 dollars to do this job. HVAC technicians are like car mechanics. They 100% overcharge for their work. My gas furnace ignitor knob recently broke because it's made out of cheap plastic. If I would have called a HVAC technician to fix it they most likely would have attempted to replace the entire valve instead of installing a new knob. I was reading online that they have to replace the entire valve because of regulations which im sure would have costed $500-$800. I purchased 2 replacement knobs for $10 dollars online. An aftermarket company makes replacements. I didn't see any replacement knobs from the manufacturer that makes the valve which im sure they do on purpose for profit and regulations. They want you to spend a bunch of money not replace a $10 dollar plastic knob. The aftermarket knob looks and works identical to the oem knob. The aftermarket knob manufacturer made a smart business decision to make those knobs because it probably only costs them a couple dollars to make them and it's something that people need. Personally if I was you I would have purchased and used some pipe dope. It's super cheap so there isn't a good reason not to use it. I also recommend spraying the lines better with water that has a good amount of dawn dishwashing liquid in it. I'm a pipefitter so I can honestly tell you that it's common for people to get leaks so you definitely want to use thread Seal Tape, pipe dope and spray it down really good with dawn dishwashing liquid/water. You honestly made a smart decision doing it yourself. Most issues with central air units and furnaces are things that you can fix on your own as long as you do some research with online videos. I've fixed multiple of these issues on my own. Back in the 90's you would have had to call a HVAC technician but now there's information and replacement parts online. I even replaced my furnace fan on my own. A HVAC technician would have probably expected me to buy an overpriced fan of their choosing and charged me hundreds to install it. If someone is considering doing this stuff on their own they need to make sure that the electric and gas are completely shut off. If you shut the electric and gas line off, find good deals online for replacement parts and watch videos it's totally worth doing it on your own. I found an used replacement fan online that looked nearly new and it saved me a ton of money. Charging $800 dollars to fix your gas valve is beyond ridiculous! $800 dollars for a hour long job is crazy! They probably purchase the parts for a cheaper price than normal, they would have drove 15min to get to your house, spent 30min to install it and another 15min to drive back to their shop so they definitely don't deserve $500-$800. I could understand if it was $300 because the valve might be $100 dollars and then $150-$200 dollars for a hour of their time but definitely not $800! What HVAC technician companies don't understand is that they lose money for charging so much because a lot of people decide to do it on their own to save money. If they would have charged you $300-$400 you probably would have decided to have them install it and they would have still made a good profit for their time.. I'm guessing a gas valve would be $50-$200 dollars so charging more than $400 dollars for the job is ridiculous. That's my personal opinion.
Me neither!
Another thing to consider is whether you’ll even be saving any money attempting this DIY yourself. Gas valve testing and replacement requires specialty tools, equipment and material that can really add up. And some of the tools and material you may not use again, unless of course you have to replace another valve.
Learning how to use these tools and materials and testing and replacing the valve itself is also a time-consuming process. A furnace gas valve making noise will require different tools and techniques than a gas valve with an electrical issue. By the time it’s all said and done, a job that would most likely take you a day or two can be done safely and professionally by an HVAC professional in much less time.
Great advice. I got lucky for sure.
A gas manometer is $50, a couple of pipe wrenches is $30, pipe dope and tape is probably $20 and the gas valve is probably around $80-$200 dollars. That's only around $200-$250 dollars which is much better than $800 dollars!!! There's plenty of videos online that teaches you how to do it. I would much rather spend a hour of time and spend $200 than to pay someone $800. I'm a pipefitter though so messing with threaded pipe and gas lines is something that I do for a living. A HVAC technician already owns those tools so charging $800 to replace this valve is ridiculous. I definitely would have replaced it on my own. I think that at least 1/3-1/2 of the population is smart enough to turn off the electric, gas and watch a couple of videos to install it themselves. Half of the population on the planet probably doesn't have enough common sense to shut off the gas/electricity or to properly tighten the pipes so I understand why some people are better off calling HVAC technicians. I understand that HVAC technicians are hard working people that are trying to make a living but $800 for this valve replacement is ridiculous. Just my opinion.
Why did you call a Tech if you're knowledgeable on valves etc 🤔
Because I am not knowledgeable about the control boards.
😂😂😂
Still working!
Wow Your not qualify to tell people how to work on their furnace
Probably not. I never told people how to fix theirs. I showed people how I fixed mine. What are your recommendations?