    A buck-boost transformer can be used for low voltage application such as lighting,control wiring or anything that requires a 12,24 or 48 volts power supply.
    buck-boost transformers can be used to obtain a proper voltage within a specified percentage.
    Here is the pdf for verifying the requirements for buck boost transformers:
    www.jeffersonelectric.com/s3/s...
    Buck-boost transformers are heavy and require good support.

Комментарии • 36

  • @debbieford8971
    @debbieford8971 9 лет назад +26

    You are wiring this transformer as a regular low voltage transformer. A buck or boost transformer has an ability to raise or drop voltage to change the supply voltage to the line of a piece of equipment after the transformer. This transformer can take the 120 volts supply and make it 96, 108, 132, or 144 volts. if you had 240 volt supply the output voltages are 216,228,252, 264 output volts depending on how you interconnect the secondary leads. This being said the rating of the transformer [ V x A ] is rated only on the differential voltage powered thru the transformer, the 12 or 24 volts used by the transformer.

  • @electricalindustry
    @electricalindustry  11 лет назад

    I added a link to the buck-boost transformer s PDF for more information in the description box.
    Thanks for watching!

  • @electricalindustry
    @electricalindustry  11 лет назад +2

    Yes check the NEC 2008 210.9 for more info. There are many options available to change your voltages. This was a transformer that was pulled out of a job that was feeding low voltage 24 v lighting. Another sparky had chosen to do it this way. Thanks for your observation.

  • @N153AX
    @N153AX 11 лет назад +8

    A few years ago, I was an apprentice working with a journeyman on a new coffee shop. Bldg was 208/120V and their fancy espresso machine reqd. 240V so off to wholesale supply and told counter guy we needed a buck/boost. The unit his computer said to give us said 32V on label, not 240V. J-man said this is wrong & cntr guy didn't know. I looked at label and figured it was giving the voltage to be added, not the final voltage. Hooked it up, and output was 240V...tricky labeling, or J-man brainfart?

  • @spelunkerd
    @spelunkerd 11 лет назад

    I was going to guess that VA was a power rating, but that wouldn't make sense if it's 5 amps on the output side. These are great little seminars, I'll watch for the one where you go into more detail about VA.

  • @dmsentra
    @dmsentra 5 лет назад

    I see the manufacturers labeling as a huge problem with buck/boost transformers. Most label the 12v/24v as Secondary Voltage(Low Voltage here) when it is in fact the Voltage Change. I spent an entire weekend scouring the web and talking to a long standing electrician and a 35 yr electrical engineer (that neither knew about buck boost) and the labeling was the only real stumbling block to understanding them. Once I figured that out the kva rating achieved was from across the drop was a smaller hurdle and I only figured that out by a B/B on Schneiders' site that listed 37kva load and a 3kva label on the same unit.

  • @b2gills
    @b2gills 11 лет назад +3

    If it only allowed going from 120v to 12v and 240v to 24v there would be only 4 wires. It could easily be wired to output 6v (wire it for 240v input, 12v output, connect to 120v source) and 48v ( wire it for 120v input, 24v output, connect to 240v source ).

  • @cabcorner1
    @cabcorner1 11 лет назад +1

    The video made it sound like you had to wire it 120v to 12v and 240v to 24v.Watch it again.You are correct about the 6v connection but I would have to check the 48v connection with the literature from the transformer to make sure the coils are rated for 240v when wired in parallel .

  • @cabcorner1
    @cabcorner1 11 лет назад +10

    I just watched it again ,you do know that you can wire that for 240v primary and 12v secondary or 120v primary and 24v secondary ?

    • @juz4kix
      @juz4kix 7 лет назад

      cabcorner1 I was thinking the same thing.

  • @cabcorner1
    @cabcorner1 11 лет назад +2

    No it's not an auto transformer . It is a isolation transformer with a 120/240v primary and a 12/24v secondary . The primary and secondary can be wired in series to create an auto transformer for bucking or boosting voltage 5 percent or 10 percent . You can wire 2 transformers together in an open delta to boost 3 phase from 208 to 230v for motor applications . When you are only adjusting voltage 5 to 10 percent I believe you can increase the kva rating of the transformer times 10 . Very handy.

    • @downtowngutter3875
      @downtowngutter3875 3 года назад

      This is an isolation step down transformer not a buck boost

  • @MrCinimod93
    @MrCinimod93 11 лет назад

    so if you were to wire it up for 240 in and 12 out but only put 120 in would you get 6 volts out

  • @prashantmadan2106
    @prashantmadan2106 7 лет назад

    What is the difference in buck boost transformer and buck boost converter?

  • @vfpaintjobs
    @vfpaintjobs 3 года назад

    I'm hooking up a 7.5 horsepower air compressor and I need to be at 2:40 which I'm running off of generac 22,500 starting in 15,000 running which gives me 240 volts but they're saying this actually 208 I'm trying to boost to 240 will this box do that for me?

  • @YVRSURF
    @YVRSURF 11 лет назад +4

    Is this not an autotransformer (typically 120, 240 or 480 Volts) and a relatively low voltage secondary (typically12, 16, 24, 32 or 48 Volts), buck-boost transformers are
    designed to be field connected as autotransformers. What you did was a total waste of money can get an xformer for so much cheaper for what you did. Where was the Buck-Boost these coils can be wired in so many configuration

  • @N153AX
    @N153AX 11 лет назад

    Sorry, my comment was not clear. Yes, it was the correct autoxfmr for the application.
    I was trying to point out that the label said 208V low volts, 32V high volts...It did not say anywhere 240V high volts. My J-man thought the autoxfmr was the wrong one until I pointed out that the label was giving # of volts to be added instead of what the final voltage would be.
    Has anyone else seen labeling like this?

  • @michaelhinchey
    @michaelhinchey Год назад

    Hi
    I need to buck down from 237v to 220v for a pneumatic elevator. The sales man stated I need this same transformer 416-1131-000.
    I feel that I would need a 16/32 secondary transformer to get me to 221v ac. What do you think?

    • @bluenation6379
      @bluenation6379 3 месяца назад

      hello, did you figure it out. i need help with it

  • @jcer85
    @jcer85 6 лет назад +4

    There is no videos showing how to increase voltage 208 to 230

    • @ITIRICI
      @ITIRICI 3 года назад

      They make them specifically for this voltage drop or increase that you mentioned

  • @GalaXy808
    @GalaXy808 6 лет назад

    What it does.this thing?

  • @GalaXy808
    @GalaXy808 10 лет назад

    Why do we need that.? Explain please!!!

  • @nema9453
    @nema9453 7 лет назад

    So since its a 240/120V Input and a 24/12V Output does this mean its a Ratio of 10 to 1 transformer (10/1)???

  • @meerscan9101
    @meerscan9101 8 лет назад

    who makes those wire strippers with crimpers?

    • @TutorialsforYouAll
      @TutorialsforYouAll 8 лет назад

      +refrigeration tech www.amazon.com/Gardner-Bender-GST-70M-Circuit-Stripper/dp/B000NGTMWS/ref=sr_1_3?ie=UTF8&qid=1454416620&sr=8-3&keywords=Circuit+Alert

  • @TomsOutside
    @TomsOutside 9 лет назад +8

    This video is pretty much a waste of time. Buck Boost says it all, while it will definitely work as a step down transformer that is not its primary use. It works as an auto transformer and is used to raise voltage by percentages, if your smart enough to connect it, many electricians never seen one, This video doesn't come close. How about connecting H1 to X1 and load, H2 to H3 connect L2 to H4and X1, connect X2 and X3, and X4 to Load as far as it doesn't matter which lead you connect to H1 and H4 if we are looking for the wave formation is it zigging or zagging, Very little info shared in this video for all the time used.

    • @hankkline7300
      @hankkline7300 3 года назад

      This is a step down transformer. It is not an auto transformer. An auto transformer has one winding with many taps like a multi-voltage HID ballast.

  • @fngmillet9381
    @fngmillet9381 4 года назад

    Been looking for wiring diagram
    How to make 235v from 208v
    All I see is 208v to 240v
    Customer was told needs to be 235v

    • @SamTheBouncer
      @SamTheBouncer 3 года назад +1

      It’s ok to wire for 240v and use for 235v

    • @jmcrate
      @jmcrate 2 года назад

      @@SamTheBouncer Agreed, +/- 5VAC is nothing, it will run up or down 5V no issues.

  • @CM-oy2kd
    @CM-oy2kd 3 года назад

    Wow. That god seimans made power supply

  • @guloguloguy
    @guloguloguy 5 лет назад +1

    IT SEEMS THAT THIS IS MERELY A TYPICAL STEP-DOWN TRANSFORMER WIRING. WHAT MAKES A "BUCK-BOOST" TRANSFORMER WIRING DIFFERENT?!...

    • @hankkline7300
      @hankkline7300 3 года назад

      When you wire the secondary in series with the primary it will reduce (Buck) or increase the voltage (boost) dependimg on the polarity.

  • @jeffreymckie3328
    @jeffreymckie3328 Год назад

    There was no buck connection made in this video. If this guy doesnt know what he is doing he should stop