What is a Chiller Economizer

Поделиться
HTML-код
  • Опубликовано: 1 окт 2024

Комментарии • 17

  • @kc5vgw
    @kc5vgw 2 месяца назад

    On the Trane cvhe and cvhf, the economizer does not pull into the suction. It is pulling into either the inlet of the second stage wheel, or 3rd wheel. Depending on if it’s a cvhe or f. On the york screws, the economizer is ported about 1.3 or 1.4x of suction. No appreciable loss as you can introduce more gas after the suction portion without adding any more load to the motor.

  • @Eighty8Fitter
    @Eighty8Fitter 5 месяцев назад +1

    Refrigeration racks use subcoolers quite often. Improving efficiency is the overall name of the game.

  • @Ingmaringmar
    @Ingmaringmar 5 месяцев назад +1

    In screw compressors the subcooler is connected to the eco port of te compressor, with a different (higher) pressure than suction pressure. (This is where the efficiency gain is). How is that for centrifugal compressors?

    • @kc5vgw
      @kc5vgw 2 месяца назад +1

      Same with a centrifugal, provided it has more than 1 stage. York yt and yk, as well as yz and YMC2 are only 1 stage of compression. However Trane uses multiple stages. And the york OM’s are multistage. Between 2 and 5 stages. Only seen 5 stage in the refineries. Usually for the PDU. Propane de asphalting unit. And they are almost always R-290 systems

  • @isaiahlewis3832
    @isaiahlewis3832 4 месяца назад

    What’s making the vapor rise to the top of the flash tank ?

    • @HVACTIME
      @HVACTIME  4 месяца назад +1

      Vapor is less dense than liquid. Vapor rises on top and the liquid collects in the bottom.

  • @HVACGUY
    @HVACGUY 5 месяцев назад

    Gree flexx hs those before liquid line to add subcooling.

  • @isaiahlewis3832
    @isaiahlewis3832 4 месяца назад

    The condenser is sending liquid refrigerant to the flash tank how is that liquid being turned into a gas ? & does it has something to do with pressurization or expansion and how ?

    • @HVACTIME
      @HVACTIME  4 месяца назад +1

      Through a expansion valve. There is a expansion valve prior to the flash tank that creates the flash gas.

    • @isaiahlewis3832
      @isaiahlewis3832 4 месяца назад

      Thank you so much & when u say create the flash gas that means changing the state correct ?

    • @HVACTIME
      @HVACTIME  4 месяца назад +1

      @isaiahlewis3832 correct, charging state

    • @Skunkhunt_42
      @Skunkhunt_42 2 месяца назад

      Yes ​@@isaiahlewis3832

  • @irfvnfaedah5776
    @irfvnfaedah5776 5 месяцев назад

    Sr ,may u help me, on york yciv
    Is there the High pressure cut out at system 1 is serial with system 3 on logic board

    • @kc5vgw
      @kc5vgw 2 месяца назад

      Yes. I think it’s due to a limitation of the digital inputs on the boards.

  • @NROhvac
    @NROhvac 5 месяцев назад

    Is it ok to think chiller economisers are similar to hot gas bypass, by the concept of keeping a load on the chiller?

    • @HVACTIME
      @HVACTIME  5 месяцев назад +1

      No, different concept

    • @NROhvac
      @NROhvac 5 месяцев назад

      @@HVACTIME ok I understand thank you