Комментарии • 134

  • @orey16
    @orey16 3 года назад +4

    Not sure why there are downvotes. This is a great video David!

    • @ElectronXLab
      @ElectronXLab  3 года назад +3

      Thanks Oscar. I appreciate the comment

  • @mohammadsamir2713
    @mohammadsamir2713 3 года назад +1

    You are explaining things like magic, thanks

  • @ohgoditsjames94
    @ohgoditsjames94 3 года назад +8

    Hi David, great video. Would it be possible to do a similar video but instead we are asked to improve the power factor from a certain value to another value but less than unity power? The example could be to improve the power factor from 0.6 to 0.9?

  • @hussainpro38
    @hussainpro38 5 лет назад +12

    "My circuit will live happily ever after"
    :)
    Thank you! helpful video.

  • @johncmitchell4941
    @johncmitchell4941 3 месяца назад

    Other calculations have wanted an efficiency rating as on a motor's tag. This suggest I can use the resistance and perhaps derive the reactance and use those numbers to size a cap.

  • @pranjalsrivastava5451
    @pranjalsrivastava5451 4 года назад +8

    so if the load is capacitive, the PFC would be an inductive reactance

    • @XTYRMIN8Z
      @XTYRMIN8Z 2 года назад +2

      In short yes, but no.
      Capacitive loads and inductive loads produce sin waves that are both out of sync with a given resistive load. The reason they neutralize each other is because inductance's wave lags behind the resistive load 90° where as capacitance's wave is 90° ahead, thus the two loads are a full 180° off of each other and thus directly nullify. Thus it is indeed yechnically possible to have a circuit with a low power factor due to a capacitive load.
      Why I say "technically" is because I don't personally know of any electrical gear / application that innately produces an unwanted and intrinsic capacitive load, and in fact none may well even exist. Inductance, however, is present in the the supply of every single electronically driven motor simply due to mere physical methods by which they operate. Thus, PFC is generally understood as adding capacitors to circuits with inductive loads rather than it being versa-vice. It's a solution to an inherent problem that can't be solved otherwise whereas the obvious solution to a circuit with too high of a capacitive load would be to remove the capacitor you added.

    • @therealdkgray
      @therealdkgray 3 месяца назад

      @@XTYRMIN8Zvery good answer.

  • @MizzAnto123
    @MizzAnto123 2 года назад +5

    Good job! Had no idea what my teacher was trying to say, but this is great and obvious.

  • @wariskn7096
    @wariskn7096 3 года назад

    Best of the best of explanation for beginners

  • @mathmath5839
    @mathmath5839 3 года назад +4

    Thank you, I had issues finding the right capacitance for the machine I built (there are ballasts in it so the PF is only 0.5)... can’t wait to remake all the calculations again !

  • @brianczuhai8909
    @brianczuhai8909 10 месяцев назад

    The inductance is a motor. The R will go down if there is resistance to the motor shaft. - The motor has a load, draws more current. Inductance will be the same. Has the same number of turns for the windings. Therefore, the capacitance will be a factor of how much the motor is loaded?

  • @tzakl5556
    @tzakl5556 5 лет назад +6

    Your explanation was simply amazing. Thank you for clearing this up for me

  • @timothychan5
    @timothychan5 Год назад

    Amazing video, thank you for the summary!

  • @victorrobertosantosclaudy7320
    @victorrobertosantosclaudy7320 6 лет назад +5

    That's was a amazing explanation

  • @jefersonmedeiros7677
    @jefersonmedeiros7677 Год назад +2

    Your channel is very good, important content and well taught. Congratulations for the initiative.

  • @muhdmustaqiim0240
    @muhdmustaqiim0240 2 года назад +1

    Hi sir i did not understand how does the final pf become =1 ? as i understand in the end of video P is 480 right and where is the new S that makes the pf=1?

  • @josepharmstrong6852
    @josepharmstrong6852 5 лет назад

    This is an awesome video thanks for making it really helped

  • @johncampbell3221
    @johncampbell3221 4 года назад

    Straight to the point !!!!!!
    Awesome

  • @phatpunxs64
    @phatpunxs64 6 лет назад +3

    watching your videos helps me brush off the.spider webs on my brain! thanks for the awesome content!

  • @mr.unknown6088
    @mr.unknown6088 4 года назад +1

    I didnt understand the last part..why would it be pf=1...after getting the capacitance. You get pf=1..pls explain.

    • @akashgupta827
      @akashgupta827 3 года назад

      bro, because the after adding the capacitor the reative power will be cancelled out as both(capacitor and inductor) will be having same values of Reactive power, and the impedance of the circuit will become purely Resistive, and you know for a purely Resistive network the power factor is UNITY!

  • @Ren-vr6jm
    @Ren-vr6jm Год назад

    i love you bro thank you so much for this video

  • @蔡鹏聪
    @蔡鹏聪 5 лет назад +3

    My brain still stuck and cant understand even watching the whole video.

    • @蔡鹏聪
      @蔡鹏聪 3 года назад

      now i understand already. Thanks for it xd

  • @dreamygirl_
    @dreamygirl_ 3 года назад

    It means power factor is always less tha 1 in both RLC series and parallel circuit?

  • @basievanwyk8686
    @basievanwyk8686 Год назад

    Hi, good day, TX for the opportunity. I am busy building a rotary phase converter, naturally the output voltage of the 380v idler motor are not gonna be equal. Can i use this formula to correct the voltage on each leg by means of run caps.please help
    TX Basie

  • @danstiurca7963
    @danstiurca7963 10 дней назад

    That is a very complicated way to say LC tank resonates at 1/sqrt(LC)
    Whole thing could take 1 minute doing it that way.

  • @renatoelamne2691
    @renatoelamne2691 Год назад

    Sir how did you get the 5 ohms and 53.13 °. Thanks

  • @davebutler3905
    @davebutler3905 Год назад

    Nice example!
    Thanks

  • @tule-hz5mj
    @tule-hz5mj 3 года назад +1

    For me, I prefer Ql=480*96*sin53.13 then C equals to 14.52 microfarad, thank for great explanation.

    • @spelunkerd
      @spelunkerd 2 года назад

      My first impression was the same, but then I realized the voltage drop across the inductor is reduced because of the resistance in series on that arm of the circuit. It's not the same as a simple LC circuit. So, you need to account for that extra resistor, the reactive power will be reduced because the resistor eats up some of the voltage drop, reducing current that will appear on that arm of the line. He conveniently used current, which builds in a correction automatically when calculating power with current , Q=I^2*R.

  • @alessandropiscozzo9904
    @alessandropiscozzo9904 6 лет назад +1

    Very nice summary... when you find S dividing P by the power factor, it might be worth saying that P is the average power delivered to the load.
    I'm writing this because often, since power is not in the same phasor domain of voltage and current, it creates confusion.... especially (to me :)) if rms quantities are needed to find non rms amplitudes
    S = Vrms x Irms
    P(t) = P + S x cos(2 x omega x t = phi)
    expression of instantaneous power delivered to the load
    from the expression above, it is evident how P is the average of the overall power which goes to the load
    P = P(t) averaged over T/2 = S x power factor
    expression of average of instantaneous power delivered to the load
    Prms = rms value of the P delivered to the load = sqrt ( (P^2) + S^2/2 )
    the expression of the Prms delivered to the load is not usually useful
    essentially this is the rms value of the instantaneous power which is a sinusoid plus its offset (P)

  • @ckindly3325
    @ckindly3325 3 года назад +2

    i really wish you were able to post more videos your lessons are very straight forward and easy to follow it's so hard to find that for these topics especially amplifiers!!

    • @ElectronXLab
      @ElectronXLab  3 года назад +4

      Thanks for your kind comments. I'm actually going to get back into making videos again soon. Stay tuned

    • @ckindly3325
      @ckindly3325 3 года назад

      @@ElectronXLab thank you for the reply I look forward to it! I've been doing everything I can going to tutoring every week and watching youtube videos and practicing as much as possible. My professor gives 0 partial credit so it has been rough...

  • @notrickross4
    @notrickross4 11 месяцев назад

    How do we know that the 9 kVAR on the capacitor and the 9 kVAR on the inductor cancel each other out? Near 6:15.

  • @md.sabirhussain237
    @md.sabirhussain237 5 месяцев назад

    What will happen if we eliminate the 3 ohm resistor?as in practice,no resistors are used in series with the load.

  • @StephenMendes
    @StephenMendes 5 лет назад

    watch the short video I just uploaded on my channel if you want to be sure you understand Power Factor Correction.... always a good idea to see another example ...... just to be sure...... plus I got playlist of projects to build ..... and lots other videos on Electronics design theory.

  • @MrLaneousEngineering
    @MrLaneousEngineering Год назад

    We are assuming the phase angle of the source is 0 degrees in these power factor formulas, could you please explain how to correct the power factor of a true parallel RLC circuit when the phase angle is not 0, say 90 degrees? I am really struggling with this at the moment. PFC could really help with alternative energy solutions in the future and your approach to this problem would be greatly appreciated. Thank You!

  • @walterbrown8694
    @walterbrown8694 5 месяцев назад

    Also, PF = cos(phase angle).

  • @MaplePatriot
    @MaplePatriot 5 лет назад +1

    This video was so damn helpful. Thank you so much!

  • @aloys234
    @aloys234 Месяц назад

    5:34 how does this calculation work on a calculator 10x2 + 9x2 becomes 13.45??? 😩

    • @ElectronXLab
      @ElectronXLab  Месяц назад

      The calculation is square root of 10*10 + 9*9...sqrt(10^2+9^2) = sqrt(181) = 13.45

  • @marliusardi9973
    @marliusardi9973 3 года назад

    hi Mr.David.
    Thank you.
    can u make vidio again about this case.
    can u solve how much Power measured, I mean Power Real Power, Apparent Power, Reactive Power and current after compensation Power factor using capacitor parallel.

  • @MultiSigen
    @MultiSigen 4 года назад

    So I keep hearing reactive power is never consumed then I hear inductors consume reactive power and capacitors supply reactive power. I’m confused. By ‘consuming’ or ‘supplying’ reactive power is one simply trying to say-causing the current to lag or lead the voltage? Coz that would be much clearer.

  • @ashlynnundlall
    @ashlynnundlall 6 лет назад

    Please explain why I sub t + I(RMS).

  • @candeegarcia4944
    @candeegarcia4944 3 года назад

    Hi, I sent an email. Thanks

  • @kautanorline4634
    @kautanorline4634 10 месяцев назад

    Sam can also cry for love

  • @sasithprabodha7626
    @sasithprabodha7626 2 года назад

    Thank you very much

  • @georgeindestructible
    @georgeindestructible 4 года назад

    Is this example (semi-)correct?
    Imagine a tube(wire) and that you want to pass an x quantity of water(current) through it(ignore time), you can pass water at any speed(voltage) as long as it's volume doesn't overwhelm the tube due to its volume, then the water passes with virtually no resistance but if we increase the volume of the water or decrease the mass the tube can manage without getting overwhelmed, then the pressure of the water inside the tube increases, so then, the tube will have to deal with that pressure(wasted thermal energy) which is why there has to be a balance, right?

  • @bowlineobama
    @bowlineobama Год назад

    Awesome. Thanks.

  • @colecarroll6145
    @colecarroll6145 Год назад

    Thank you so much

  • @Swenser
    @Swenser Год назад

    I've seen power factor correction circuits rather than just a simple parallel cap. What's that all about?

    • @ElectronXLab
      @ElectronXLab  Год назад

      You might be referring to active power factor correction circuits which directly measure the voltage and or current and use a switching circuit to actively correct for low power factor. The main advantage is that power factor will be corrected even as the load changes. The main disadvantage is that the circuit is much more complex.

  • @ferdinvivian9336
    @ferdinvivian9336 5 лет назад +2

    how to convert 3+j 4 ohms = 5 ohms 53.13 degree angle

  • @dylanreen1629
    @dylanreen1629 4 года назад

    3:33 42.1k/480=87 you wrote that but typed into your calculator p/v, 40k/480 =83

  • @byBrazzily
    @byBrazzily 3 года назад

    why did 53,15 degres become -53,15 degres?

  • @thedavesofourlives1
    @thedavesofourlives1 3 года назад

    Very cool explaination. What about opposite PF, where there is an over capacitance creating what i assume would be a leading PF

  • @stevenolsen6360
    @stevenolsen6360 4 года назад

    if only there was a chart for domestic appliances like fluorescent lights

  • @qzorn4440
    @qzorn4440 2 года назад

    sweet info, do you have a workbook? thanks

  • @howcreated_ideas
    @howcreated_ideas 3 года назад

    Nice topic....

  • @EVERY.CIRCUIT
    @EVERY.CIRCUIT 3 года назад

    Thank you so much

  • @zodd1790
    @zodd1790 Год назад

    how do I put omega function in calculator?

  • @sohailjanjua123
    @sohailjanjua123 3 года назад

    Hi David, I like your lecture. Thanks

  • @Greg_Chase
    @Greg_Chase Год назад

    I would plead that this be viewed by all the 'over unity' hobbyists who believe they have found greater output power than input power because they fail to account for the affects of V and I phase difference caused by inductor/capacitor in the circuit.
    The majority of these folks (1) use a multimeter (only) to measure output current and output voltage, then (2) multiply them together and believe they have discovered more output power than input power.
    A common example: Faraday's law shows that if you discharge an inductor very abruptly, the back EMF voltage spike can be quite high - since time (dt) is in the denominator:
    E = di / dt (Faraday's law)
    Using a MOSFET to very abruptly interrupt current flow in a coil creates a large back EMF spike (which is the reason 'snubber' diodes are popular!) and nearly all 'over unity' hobbyists then multiply this temporary large voltage spike by current flow and calculate an immense power value which greatly exceeds input power.
    I've tried explaining the issue to these guys, some of whom spend years, literally, not knowing Faraday's law and the difference between real and apparent power. Your video I believe would help them understand why reactive components change the power delivered to the load - it is about the clearest explanation I've found - good job on your part.

  • @soewunnamyo2703
    @soewunnamyo2703 5 лет назад

    Your video is total impedance formula from 3+j 4 ohm what means is value of j

    • @RealistRanting
      @RealistRanting 4 года назад

      J is an imaginary number, in maths it’s called i. do some more YouTubing 👍

  • @kevinlinsley9594
    @kevinlinsley9594 3 года назад

    Its kind of dumb that you don't show the formula your using. Instead you just plug in the values without any regard that your audience might get lost

    • @SimEon-jt3sr
      @SimEon-jt3sr 9 месяцев назад

      Dude the title is power factor correction. If you know what that means you gotta be able to look up the formulae yourself. Would you rather not hear some with knowledge to share? Maybe they don't have video editing software but still decide to share their know how. You want them to do the work for you?

  • @samueladitya1729
    @samueladitya1729 3 года назад

    I still dont understand if capacitor have impedance and current pass through it, doesn't it consume power too and wasted?

    • @ElectronXLab
      @ElectronXLab  2 года назад

      An ideal capacitor doesn't consume power. It's just like an electron storage container, you can fill it up with electrons to store energy and then release all the electrons to release energy

  • @Abdelhamid_Helal
    @Abdelhamid_Helal 4 года назад

    On which programme do you use to write ?

  • @kirandewoo5390
    @kirandewoo5390 5 лет назад

    Wow 12 mins worked out 12 months. Again thanks a lot Sir.

  • @scottwilliams7483
    @scottwilliams7483 4 года назад

    this was very helpful thanks for posting

  • @ExtremeEngineering
    @ExtremeEngineering 4 года назад

    Thanks

  • @altuber99_athlete
    @altuber99_athlete 5 лет назад

    Amazing video! One observation, though. At 10:40, are you sure Q = V^2/X? I once tried to prove that equation, but I concluded that was false. So, can you please prove it?

    • @alexjuarez6700
      @alexjuarez6700 5 лет назад +1

      The pizza lol. Well, this is really the power equation P=V*I but we know I=V/R so we sub that in to the power equation and we get P=V*(V/R) or P=V^2/R. He’s dealing with imaginary power so he’s using Q instead of P and X instead of R. Hope this helps.

  • @dannyozuna
    @dannyozuna Год назад

    I have forgotten all these math algorithms!

  • @stroomchannel6508
    @stroomchannel6508 3 года назад

    Good explaination...👍

  • @hamzaaabouz3711
    @hamzaaabouz3711 3 года назад

    Thank You David , good Job

  • @ovidius2000
    @ovidius2000 Год назад

    afterAddingCapacitor,TheCurrentInCoilIncreases.SoTheCoilCouldBurn,IfPowerFactorIsTooHigh?

  • @kamalabouzhar8469
    @kamalabouzhar8469 4 года назад

    amazing explanation.Thx

  • @Mark_Won
    @Mark_Won 2 года назад

    @7:50 2pi x 10.6 does not equal 4 (ohms) regardless of the order of magnitude. What's going on here?

    • @ElectronXLab
      @ElectronXLab  2 года назад +1

      I think you missed the 60.
      2pi x 60 x 10.6 = 4 Ohms

    • @Mark_Won
      @Mark_Won 2 года назад

      Well that's embarrassing!

  • @PheonixHDz
    @PheonixHDz 4 года назад

    This is very useful, thank you.

  • @sbonelobonengcongo2262
    @sbonelobonengcongo2262 5 лет назад

    THANKS A LOT BUT IM CONFUSED HERE WHY Qc should be = QL ??? HELP PLC

  • @abudhakir9403
    @abudhakir9403 4 года назад

    Great work,thanks lot...

  • @trinhpcb1528
    @trinhpcb1528 5 лет назад

    where is the 96A?

  • @bellobellob7552
    @bellobellob7552 2 года назад

    well-done

  • @caleb7799
    @caleb7799 2 месяца назад

    why can't you clear your throat when it becomes filled with mucus?

  • @rollmeister
    @rollmeister 3 года назад

    So power factor has to be corrected with a specific capacitor for a given load & pf?

    • @thedavesofourlives1
      @thedavesofourlives1 3 года назад

      Unless it's the opposite type what i think is called a "leading" rather than this "lagging" current.

  • @AJ-et3vf
    @AJ-et3vf 2 года назад

    awesome video sir! THank you!

  • @yomaljayasinghe2435
    @yomaljayasinghe2435 5 лет назад

    Please I would like to know the screen writing tool you used for this video. Is it a pen of some kind??

    • @ElectronXLab
      @ElectronXLab  5 лет назад

      For this video I think I used a Wacom tablet. For more recent videos, I use a OneNote on a MS Surface tablet

  • @andr5919
    @andr5919 5 лет назад

    Great, with a PF of 1 we get full resonance with massive resonance voltages

  • @technology8436
    @technology8436 5 лет назад

    Wow

  • @technology8436
    @technology8436 5 лет назад

    Wow

  • @gretawilliams8799
    @gretawilliams8799 5 лет назад

    S

  • @impactodelsurenterprise2440
    @impactodelsurenterprise2440 4 года назад

    Does using a power correction capacitor results in more kW being drawn from the grid just so we can sync the voltage and current? I mean it can't be free right? There're gotta be some kind of losses?

    • @ElectronXLab
      @ElectronXLab  4 года назад +1

      No, counterintuitively adding the new component will result in lower losses (for the same amount of real power to the load). The power factor correction means the apparent power will be less and so the the peak current will be less. The lower peak current means there will be lower resistive losses in the wires.

    • @impactodelsurenterprise2440
      @impactodelsurenterprise2440 4 года назад

      @@ElectronXLab Say I have a machine that consumes 10kwh and 10kvarh as registered on the electric meter per hour, and therefore has a power factor of 0.71. If I were to correct it to 0.9, the meter would now register 10kwh and 5kvarh per hour?

    • @thedavesofourlives1
      @thedavesofourlives1 3 года назад

      @@impactodelsurenterprise2440 it would cost less to run if you increase the PF toward 0.99

  • @michaelweiser9457
    @michaelweiser9457 4 года назад

    Since reactive power is I^2 * X, how come the capacitor's reactance isn't -4? (to offset Xl = 4)

    • @PheonixHDz
      @PheonixHDz 4 года назад

      Because that's impossible. The minus in this case is technically an imaginary number and only serves to represent that it has the opposite effect to an inductor.

    • @philipriesling3897
      @philipriesling3897 4 года назад +1

      Because the current in the C leg is not the same as the current through R and L.That makes capacitor's reactance different. If C was in series with R & L then Yes that would've been the case.

  • @justinbieber19010
    @justinbieber19010 5 лет назад

    How did you decide to place the capacitor in parallel to the other circuit elements as opposed to in series? Of course it is helpful to do so to know the voltage across it, but for example how is its power factor correction ability altered if a capacitor was placed in series with the inductor?

    • @ElectronXLab
      @ElectronXLab  5 лет назад

      You could do a similar calculation to see what capacitor you need placed in series. Practically speaking, it is far easier to place a capacitor in parallel to the circuit than in series with it.

    • @justinbieber19010
      @justinbieber19010 5 лет назад

      @@ElectronXLab thank you! Also, when placing the capacitor in parallel with the other load, there would be a division of current between the capacitor and the resistor-inductor pair- would this result in less reactive power being consumed by the inductor, since Q=I^2 * X(inductor)?

    • @ElectronXLab
      @ElectronXLab  5 лет назад +1

      @@justinbieber19010 The capacitor is in parallel with the RL pair and also in parallel with the voltage source. This means (assuming an ideal voltage source ) that the voltage across the RL branch will stay the same

  • @emadsamir6092
    @emadsamir6092 5 лет назад

    very helpful playlist and life saver for the exam, i want to ask why we added the capacitance in parallel not in series with the inductance and the resistance?

    • @ElectronXLab
      @ElectronXLab  5 лет назад

      It's easier to physically place the capacitor there. You don't have to break the circuit and you can do it right at the power supply.

    • @souvikdas2009
      @souvikdas2009 2 года назад +1

      @@ElectronXLab So, will the apparent power change if we put capacitor in series with resistance?

    • @ALAL-jm1lr
      @ALAL-jm1lr 2 года назад +1

      @@souvikdas2009 if u put in series, then u change current to machine or circuit that it needs...so the only option to place in parrallel so u dont affect the original machine or circuit requirments.

  • @igotbev1394
    @igotbev1394 4 года назад

    Thanks 🐕

  • @T-She-Go
    @T-She-Go 6 лет назад

    That was great, thank you!!

  • @Tsykal
    @Tsykal 2 года назад

    4:02 real power, not apparent.

  • @BATMEX44
    @BATMEX44 5 лет назад

    why is too much voltage in the secondary instead of 13v dc I got 33v dc and capacitors overheating ? help me somebody

    • @ElectronXLab
      @ElectronXLab  5 лет назад

      I'm not sure what you are asking. There is no secondary in this example.

    • @BATMEX44
      @BATMEX44 5 лет назад

      @@ElectronXLab ok. thanks too much weed.!

    • @thedavesofourlives1
      @thedavesofourlives1 3 года назад

      if you're trying to convert AC to DC with a transformer and rectifier, you multiply the RMS Ac volts by about 1.4, so to charge a 12v battery for example, you only need about a 9v AC transformer/rectifier combo.

  • @jakehealthx
    @jakehealthx 4 года назад

    Just a quick question. when you calculated the reactive power of the inductor (96)^2 * 4. I noticed you used a current value of 96 amps. Isn't it true that once you add the capacitor the current through the inductor will no longer be the 96 amps and instead will be divided between the two branches. I guess I'm just confused on how the reactive power of the inductor will stay the same after connecting the capacitor.

    • @ElectronXLab
      @ElectronXLab  4 года назад

      The voltage across the R-L branch of the circuit will not change, so the current will not change either.